(Msg. 1) Posted: Tue Jan 13, 2004 12:19 pm
Post subject: First time APC BACK-UPS user needs help with the Building wiring fault indicator
Archived from groups: alt>comp>hardware (more info?)

I bought a APC BACK-UPS RS 800VA 120V and love it! In the spring time
and early summer (believe it or not) I get a lot of power brownouts.
The power company claims that squirrels are most of the cause of it
(LOL).

Anyway I carefully followed the instructions but still see
the Building wiring fault indicator in red. I don't have three pronged
outlets (old complex) so I grounded using the plate screw. Is this
right? Should I be concerned? The unit runs perfectly though. I had an
occurrence to see the APC in action a few days ago and my PC never
batted a eye during the incident


P.S. I used a two prong adaptor with an grounding wire.

TIA

 >> Stay informed about: First time APC BACK-UPS user needs help with the Building .. 
Back to top
Login to vote
John McGaw

External


Since: Jan 05, 2004
Posts: 22



(Msg. 2) Posted: Tue Jan 13, 2004 12:19 pm
Post subject: Re: First time APC BACK-UPS user needs help with the Building wiring fault indic [Login to view extended thread Info.]
Archived from groups: per prev. post (more info?)

"Dunny Rummy" <fdsss.DeleteThis@dfdsf.com> wrote in message
news:n8d700tmosqgj8sgiavrjanuihq631o460@4ax.com...
 > I bought a APC BACK-UPS RS 800VA 120V and love it! In the spring time
 > and early summer (believe it or not) I get a lot of power brownouts.
 > The power company claims that squirrels are most of the cause of it
 > (LOL).
 >
 > Anyway I carefully followed the instructions but still see
 > the Building wiring fault indicator in red. I don't have three pronged
 > outlets (old complex) so I grounded using the plate screw. Is this
 > right? Should I be concerned? The unit runs perfectly though. I had an
 > occurrence to see the APC in action a few days ago and my PC never
 > batted a eye during the incident
 >
 >
 > P.S. I used a two prong adaptor with an grounding wire.
 >
 > TIA

If your UPS uses a single indicator to show problems it isn't going to be
any help in determining what the problems might be. The best suggestion I
can give is to buy one of the simple outlet testers sold at every hardware
store and home center. These typically have three indicators on them and
along with a chart will indicate exactly what is wrong. You should be
prepared for the worst though -- the problem is likely to be something that
requires at least opening and re-wiring your outlet(s) and/or it may require
running new wires from the panel and providing a proper ground point.
--
John McGaw
[Knoxville, TN, USA]

Return address will not work. Please
reply in group or through my website:
<a style='text-decoration: underline;' href="http://johnmcgaw.com" target="_blank">http://johnmcgaw.com</a><!-- ~MESSAGE_AFTER~ -->

 >> Stay informed about: First time APC BACK-UPS user needs help with the Building .. 
Back to top
Login to vote
Wayne Morgan

External


Since: Jan 13, 2004
Posts: 50



(Msg. 3) Posted: Tue Jan 13, 2004 2:27 pm
Post subject: Re: First time APC BACK-UPS user needs help with the Building wiring fault indic [Login to view extended thread Info.]
Archived from groups: per prev. post (more info?)

The UPS is also a surge suppressor. It will use the 3rd wire ground to route
any surges through. You probably don't have sufficient ground on the screw.
Another thing that can cause the light to be on is high neutral voltage, a
common problem in old buildings. The UPS part ought to work, the problem is
going to be with the surge suppression. Also, there may be some other
problem in the building wiring that could cause a problem for the entire
building, depending on what it actually is.

--
Wayne Morgan


"Dunny Rummy" <fdsss.RemoveThis@dfdsf.com> wrote in message
news:n8d700tmosqgj8sgiavrjanuihq631o460@4ax.com...
 > I bought a APC BACK-UPS RS 800VA 120V and love it! In the spring time
 > and early summer (believe it or not) I get a lot of power brownouts.
 > The power company claims that squirrels are most of the cause of it
 > (LOL).
 >
 > Anyway I carefully followed the instructions but still see
 > the Building wiring fault indicator in red. I don't have three pronged
 > outlets (old complex) so I grounded using the plate screw. Is this
 > right? Should I be concerned? The unit runs perfectly though. I had an
 > occurrence to see the APC in action a few days ago and my PC never
 > batted a eye during the incident
 >
 >
 > P.S. I used a two prong adaptor with an grounding wire.
 >
 > TIA<!-- ~MESSAGE_AFTER~ -->
 >> Stay informed about: First time APC BACK-UPS user needs help with the Building .. 
Back to top
Login to vote
Dunny Rummy

External


Since: Jan 13, 2004
Posts: 15



(Msg. 4) Posted: Tue Jan 13, 2004 5:26 pm
Post subject: Re: First time APC BACK-UPS user needs help with the Building wiring fault indic [Login to view extended thread Info.]
Archived from groups: per prev. post (more info?)

I rent in this apt complex
So rewiring might be out of the question. Maybe there is a way to run
a ground wire but from where to where?
The breaker box is just 2 feet from where the UPS is pluged in. A
coworker said if I can find a water pipe I can run a wire from the
water pipe to the outlet where the UPS is pluged in. Is this true?
What am I looking for with this outlet tester?
TIA


On Tue, 13 Jan 2004 07:26:38 -0500, "John McGaw" <nowhere.DeleteThis@all.xyz>
wrote:

 >"Dunny Rummy" <fdsss.DeleteThis@dfdsf.com> wrote in message
 >news:n8d700tmosqgj8sgiavrjanuihq631o460@4ax.com...
  >> I bought a APC BACK-UPS RS 800VA 120V and love it! In the spring time
  >> and early summer (believe it or not) I get a lot of power brownouts.
  >> The power company claims that squirrels are most of the cause of it
  >> (LOL).
  >>
  >> Anyway I carefully followed the instructions but still see
  >> the Building wiring fault indicator in red. I don't have three pronged
  >> outlets (old complex) so I grounded using the plate screw. Is this
  >> right? Should I be concerned? The unit runs perfectly though. I had an
  >> occurrence to see the APC in action a few days ago and my PC never
  >> batted a eye during the incident
  >>
  >>
  >> P.S. I used a two prong adaptor with an grounding wire.
  >>
  >> TIA
 >
 >If your UPS uses a single indicator to show problems it isn't going to be
 >any help in determining what the problems might be. The best suggestion I
 >can give is to buy one of the simple outlet testers sold at every hardware
 >store and home center. These typically have three indicators on them and
 >along with a chart will indicate exactly what is wrong. You should be
 >prepared for the worst though -- the problem is likely to be something that
 >requires at least opening and re-wiring your outlet(s) and/or it may require
 >running new wires from the panel and providing a proper ground point.<!-- ~MESSAGE_AFTER~ -->
 >> Stay informed about: First time APC BACK-UPS user needs help with the Building .. 
Back to top
Login to vote
philo

External


Since: Feb 08, 2004
Posts: 687



(Msg. 5) Posted: Tue Jan 13, 2004 5:26 pm
Post subject: Re: First time APC BACK-UPS user needs help with the Building wiring fault indic [Login to view extended thread Info.]
Archived from groups: per prev. post (more info?)

"Dunny Rummy" <fdsss.TakeThisOut@dfdsf.com> wrote in message
news:ptv700lqo24pvij4m5ff0b2k709jugijjv@4ax.com...
 > I rent in this apt complex
 > So rewiring might be out of the question. Maybe there is a way to run
 > a ground wire but from where to where?
 > The breaker box is just 2 feet from where the UPS is pluged in. A
 > coworker said if I can find a water pipe I can run a wire from the
 > water pipe to the outlet where the UPS is pluged in. Is this true?
 > What am I looking for with this outlet tester?
 > TIA
 >


It's possible the plug is not polarized correctly
unplug it and flip it around. It the red light is still on then put it back
the way it was as evidently there is a grounding propblem<!-- ~MESSAGE_AFTER~ -->
 >> Stay informed about: First time APC BACK-UPS user needs help with the Building .. 
Back to top
Login to vote
ChrisJ9876

External


Since: Jan 05, 2004
Posts: 19



(Msg. 6) Posted: Tue Jan 13, 2004 6:19 pm
Post subject: Re: First time APC BACK-UPS user needs help with the Building wiring fault indic [Login to view extended thread Info.]
Archived from groups: per prev. post (more info?)

 >From: "Wayne Morgan" comprev_gothroughthenewsgroup DeleteThis @hotmail.com
 >Date: 01/13/2004 6:27 AM Eastern Standard Time
 >Message-id: <fCQMb.7719$m92.5353@newssvr22.news.prodigy.com>
 >
 >The UPS is also a surge suppressor. It will use the 3rd wire ground to route
 >any surges through. You probably don't have sufficient ground on the screw.
 >Another thing that can cause the light to be on is high neutral voltage, a
 >common problem in old buildings. The UPS part ought to work, the problem is
 >going to be with the surge suppression. Also, there may be some other
 >problem in the building wiring that could cause a problem for the entire
 >building, depending on what it actually is.
 >
 >--
 >Wayne Morgan
 >
 >
 >"Dunny Rummy" <fdsss DeleteThis @dfdsf.com> wrote in message
 >news:n8d700tmosqgj8sgiavrjanuihq631o460@4ax.com...
  >> I bought a APC BACK-UPS RS 800VA 120V and love it! In the spring time
  >> and early summer (believe it or not) I get a lot of power brownouts.
  >> The power company claims that squirrels are most of the cause of it
  >> (LOL).
  >>
  >> Anyway I carefully followed the instructions but still see
  >> the Building wiring fault indicator in red. I don't have three pronged
  >> outlets (old complex) so I grounded using the plate screw. Is this
  >> right? Should I be concerned? The unit runs perfectly though. I had an
  >> occurrence to see the APC in action a few days ago and my PC never
  >> batted a eye during the incident
  >>
  >>
  >> P.S. I used a two prong adaptor with an grounding wire.
  >>
  >> TIA
 >
 >

If it's an old building with old wiring, it's possible that the outlet box is
not grounded at all; if so, the wire you attached to the plate screw is not
connected to ground.<!-- ~MESSAGE_AFTER~ -->
 >> Stay informed about: First time APC BACK-UPS user needs help with the Building .. 
Back to top
Login to vote
Dunny Rummy

External


Since: Jan 13, 2004
Posts: 15



(Msg. 7) Posted: Tue Jan 13, 2004 7:04 pm
Post subject: Re: First time APC BACK-UPS user needs help with the Building wiring fault indic [Login to view extended thread Info.]
Archived from groups: per prev. post (more info?)

Is there a way to fix this if it is the problem?
I just want make sure my APC BACK-UPS will be able to carry out in the
event of a black out or brownout. I get frustrated when I lose work
when brownouts happen (though minnor).
TIA!


On Tue, 13 Jan 2004 09:14:28 -0600, "philo" <philo RemoveThis @privacy.net> wrote:

 >
 >"Dunny Rummy" <fdsss RemoveThis @dfdsf.com> wrote in message
 >news:ptv700lqo24pvij4m5ff0b2k709jugijjv@4ax.com...
  >> I rent in this apt complex
  >> So rewiring might be out of the question. Maybe there is a way to run
  >> a ground wire but from where to where?
  >> The breaker box is just 2 feet from where the UPS is pluged in. A
  >> coworker said if I can find a water pipe I can run a wire from the
  >> water pipe to the outlet where the UPS is pluged in. Is this true?
  >> What am I looking for with this outlet tester?
  >> TIA
  >>
 >
 >
 >It's possible the plug is not polarized correctly
 >unplug it and flip it around. It the red light is still on then put it back
 >the way it was as evidently there is a grounding propblem
 ><!-- ~MESSAGE_AFTER~ -->
 >> Stay informed about: First time APC BACK-UPS user needs help with the Building .. 
Back to top
Login to vote
philo

External


Since: Feb 08, 2004
Posts: 687



(Msg. 8) Posted: Tue Jan 13, 2004 7:04 pm
Post subject: Re: First time APC BACK-UPS user needs help with the Building wiring fault indic [Login to view extended thread Info.]
Archived from groups: per prev. post (more info?)

"Dunny Rummy" <fdsss RemoveThis @dfdsf.com> wrote in message
news:bf5800ls67fra6ckudlid861j15l29itfb@4ax.com...
 > Is there a way to fix this if it is the problem?

Yes! the outlet needs to be properly polarized and grounded.

 > I just want make sure my APC BACK-UPS will be able to carry out in the
 > event of a black out or brownout. I get frustrated when I lose work
 > when brownouts happen (though minnor).
 > TIA!
 >
 >

If you use the UPS as it is presently...you may still have brownout
protection...
but there is definately a safety issue.

Although you landlord *should* pay to have an electrician repair it...
for the purpose of safety...maybe you could offer to pay half. It's a
relatively
minor job.<!-- ~MESSAGE_AFTER~ -->
 >> Stay informed about: First time APC BACK-UPS user needs help with the Building .. 
Back to top
Login to vote
w_tom

External


Since: Dec 10, 2003
Posts: 416



(Msg. 9) Posted: Wed Jan 14, 2004 12:27 pm
Post subject: Re: First time APC BACK-UPS user needs help with the Building wiring [Login to view extended thread Info.]
Archived from groups: per prev. post (more info?)

Safety ground is unrelated to battery backup - from
blackouts and brownouts. Most common failure of a UPS is dead
battery. These plug-in UPSes tend to lose batteries in but a
few years - rapid battery failure. Test is quite simple. Use
computer with battery backup unplugged from wall receptacle.
If computer works for many minutes, then battery inside
battery backup is OK.

That ground light does nothing for transient protection. In
fact, that APC UPS does not even claim to protect from
destructive transients. Read their specs (if even
available). It claims no common mode transient protection;
which is irrelevant to that red warning light.

That red 'missing ground' light is reporting a human safety
problem and a possible threat to interconnected electronics.
Your receptacles are only two prong because no safety ground
wire exists. Using the receptacle screw will do nothing
because that safety ground wire is not installed. Only
solution is to run a safety ground wire from breaker box.
Even grounding to a cold water pipe is a bad and completely
unacceptable solution; may create a threat to human safety;
and not even sufficient as an earth ground.

Note the difference - safety and earth grounds. That wall
receptacle is missing a safety ground which is different from
earth ground. Earth ground is necessary for transient
protection. That red light can not report and does not even
claim to test the existence of earth ground. That red light
reports a human safety and other potential problems.

Dunny Rummy wrote:
 > Is there a way to fix this if it is the problem?
 > I just want make sure my APC BACK-UPS will be able to carry out in the
 > event of a black out or brownout. I get frustrated when I lose work
 > when brownouts happen (though minnor).
 > TIA!<!-- ~MESSAGE_AFTER~ -->
 >> Stay informed about: First time APC BACK-UPS user needs help with the Building .. 
Back to top
Login to vote
CBFalconer

External


Since: Mar 11, 2004
Posts: 616



(Msg. 10) Posted: Wed Jan 14, 2004 10:34 pm
Post subject: Re: First time APC BACK-UPS user needs help with the Building wiring [Login to view extended thread Info.]
Archived from groups: per prev. post (more info?)

w_tom wrote:
 >
 > Safety ground is unrelated to battery backup - from
 > blackouts and brownouts. Most common failure of a UPS is dead
 > battery. These plug-in UPSes tend to lose batteries in but a
 > few years - rapid battery failure. Test is quite simple. Use
 > computer with battery backup unplugged from wall receptacle.
 > If computer works for many minutes, then battery inside
 > battery backup is OK.

Speaking of UPSs, I have here a non-functional APC 420 Backup Pro
that I picked up for $5 at a tag sale. I suspect it needs only a
battery. Can I try it out with something like a car battery
hooked in to check, and if it flies where does one go for a new
internal battery?

Meanwhile an APC BE350, which came from a Staples close-out at
about $30, is doing fine. I also have old wiring with 2 pin
plugs, so the power fault is always on. It gives me about 5 to 10
minutes to shut down.

--
Chuck F (cbfalconer@yahoo.com) (cbfalconer@worldnet.att.net)
Available for consulting/temporary embedded and systems.
<http://cbfalconer.home.att.net> USE worldnet address!<!-- ~MESSAGE_AFTER~ -->
 >> Stay informed about: First time APC BACK-UPS user needs help with the Building .. 
Back to top
Login to vote
Display posts from previous:   
   Hardware Problem Solving Community! (Home) -> General Discussion All times are: Pacific Time (US & Canada) (change)
Page 1 of 1

 
You can post new topics in this forum
You can reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum



[ Contact us | Terms of Service/Privacy Policy ]